power vents and turtle backs
« Back To Roofers TalkHere's one to ponder. My customer has two power vents installed right below the ridge. These vents are the only sources of roof ventilation. I measured the ridge footage and concluded that we could install about 120 feet of ridge vent, which I think would do a hell of a lot of work than just the two power vents which sit within 10 feet of one another. Customer agrees, then argues that $6 a foot for plastic ridge vent is too expensive. Do you guys agree?
More interesting is his opinion that he should leave the power vents in. Left in and disconnected, according to him, they will function the same as turtle backs (low profiles). He's so convinced of this that he wants to add a THIRD power vent that he has laying around in the attic.. It has no motor.. He just wants to hook it up and "use it as a turtle." I have never read that a power vent not running would operate the same as a low profile.. Does anyone want to put in their two cents? I'd be much obliged.
I would'nt argue with him sounds like he has the "Know IT All Attitude" Just tell him you will throw in some low profile turtle vents for free and get them old ones off the roof.
Unless of course he has some decking problems due to bad ventilation
I tried that, and he said I wasn't following his "line of thinking.." He seems insistent on leaving those power vents in, since they function the same as turtle vents.. But is that really true? Disconnected, the power vents do the same thing?
Good morning.
In general, it's possible to be friendly,polite and business-like-while maintaining controll of the situation. In the scenario you described- it looks like you don't have control of the situation :)
Simply put- you can't let the customer design a roof system that YOU will be held responsible for-via a warranty,implied or otherwise.
Explain to the customer- that with a ridge vent-in order to have it work properly,all other vents( power fans, slant backs, gable end vents etc.) need to be blocked off/eliminated. Only the ridge vent ,balanced by soffit vents should remain.
If you don't follow this procedure- you can get into some freaky situations where things are working backwards-air( and snow,and rain) be sucked IN from ridge vents etc.
Since YOU are going to be responsible for the project- it must be done to YOUR specifications- not the customers. If he won't allow you to do it YOUR way- don't do it at all.
regaurding platic ridge vents:- for many years- MANY-when using ridge vents we used the corrogated plastic type, primarily because they were very un-obtrusive.- within the last year we have had 2 seperate installations "back flow". 2 installations in 20 plus years-is 2 too many-and so now,if using ridge vents we will ONLY use baffled designs. In retrospect- the 2 problem installations were not balanced with soffit vents as well as I would have liked. ALL of our work is old house work-and soffit ballanced intake is not always practical. In retrospect- slant backs may have been a better choice.
Best wishes to you, stephen
Have you ever fired a customer? This sounds like a situation where I would walk away from a job as he doesn't want to listen to the expert in his field. What Stephen said explains everything. And $6.00 per foot may or not be to much. Depends on what your overhead is, how long it will actually take to do the job, and how much profit you should be making. Roofing companies that use a per ft. per square price on their pricing generally loose a ton of money before they realize what they have done. The only proper way to bid is a time based estimate. Though that is only my opinion.
Heck, if he would have called our company we charge for repair estimates anymore. Why jump through hoops for things that are less than $2,000.00 generally. Homeowners that want to shop can do that to the jacklegs. Serious people will have no problem paying for your time and expertise.
Good luck in whatever you do.
Stephen is right. Explain to him that air is "lazy" and that it will flow to the point of least resistance. With the power vents running, all that will happen is that since they are nearest the peak vent, the peak vent will become the intake; and that will "short circuit" the "system" and it will not work at all. You cannot mix the different types of ventilation without consequences.
Soffit vents will work with turtle vents and soffit vents will work with power vents and soffit vents will work with a ridge vent, but the ridge and power vents and turtle vents will not work with each other. Something has to give. If he won't change his tune, it should be you saying good bye!
In a way, the customer is right, the holes for the power vents will function like a turtle vent-under certain conditions. In a high heat situation with no wind, they probably will exhaust additional hot air. But moving air is lazy, it will take the pathway of least resistance and that probably will be in the turtle vent and out the ridge vent, disrupting the flow from soffit vents to the ridge vents.
1.The power vent without power will work better than the slant back. Without wind, just because it is larger. With wind, because air flowing over the large dome will create low pressure and draw air no matter the wind direction.
2. Ridge vents will work with turtle/slant backs. Without wind, the heat/high pressure in the attic will push out of any exhaust hole. With wind, the airflow/low pressure that is acting on the ridge is also acting on the static vent. Drawing air which equals resistance.
3. A power vent will work right next to a ridge vent. Given adequate soffit intake. Within 3 feet of a typical power vent the air velocity is approximately 2mph. And the airflow/draw direction is mostly directly perpendicular to the vent.
Dennis, I can see what you are saying - But by adding the power vent you are rendering the ridge vent as well as gable vents useless - the experiment as well does not show where that inside smoke is coming from and if the soffit vents work properly which i would assume they do - but if they were not to work or were accidentally plugged. then i am sure the least resistance would come from the gable or ridge or conditioned space. (why take the risk?)
Here in MN the ventilation is most important in the winter months i wish they would make a temp controll that corresponded with the outside air temp -- so if it is 30 out side the fan would run until it is 30 inside the unconditioned space or within a 5-10 degree difference.
As far as the original post - If the ridge vent has to high of price tag and he wants to keep his power vents as static vents - I WOULD have a problem with it - Only because a vent is a serviceable item that we must take responsibility for and i would prefer they were replaced with new static vents so there is no question as to the condition of the new roof we are installing. Thus rendering the whole performance issue a moot point ( weather a power vent unplugged works as good as or better that a regular turtle vent)
As well as the code is met - and there are no signs / problems with moisture in the attic previously.
$6 a ft ??????????????????
Let someone lose money on this deal
Yeah, I forgot. We charge between $9 and $10.00 per foot!
Wow everyone has such great input. Minnesota: you brought up a good point.. I don't want to be responsible for old vents. But since they won't even be running I assume there isn't too much that could go wrong there.
wywoody Said: In a way, the customer is right, the holes for the power vents will function like a turtle vent-under certain conditions. In a high heat situation with no wind, they probably will exhaust additional hot air. But moving air is lazy, it will take the pathway of least resistance and that probably will be in the turtle vent and out the ridge vent, disrupting the flow from soffit vents to the ridge vents.
So Survivor you're saying that it's probable that the turtle vent will draw in hot air from outside (as in, hot air from the rooftop)? And then the ridge vent will push it out? Not sure I get it. Please explain what you mean.
Oh and Dennis thank you much for your input.. I have also read your posts on roofer.com and you are quite the advocate of the "Short Circuit Myth." My sister is a physics major and she and I have been discussing it, as well. I agree that the ridge vent and power vent could work together, but I don't feel experienced enough to be judge whether or not the soffit ventilation is adequate on each and every home that I roof.. And therefore I'd rather not take the chance just yet.
"Here in MN the ventilation is most important in the winter months i wish they would make a temp controll that corresponded with the outside air temp -- so if it is 30 out side the fan would run until it is 30 inside the unconditioned space or within a 5-10 degree difference."
I like that idea.
"I agree that the ridge vent and power vent could work together, but I don't feel experienced enough to be judge whether or not the soffit ventilation is adequate on each and every home that I roof.. And therefore I'd rather not take the chance just yet."
That makes sense too.
Well in my experience triing to re -use old vents is counter productive -- tearing off cleaning them up -- holes where nailed storing them someplace until driied in then you never know if a seam or a crack or a dent will go bad? then probably have to paint - and they will still look like crap - crew whineing why did'nt he just pay $20.00 for new ones then your competitor sees it when bidding job next door and tells that homeowner -- we dont re -use anything everything is new - that guy probably uses cheap labor anything for a buck --- etc....